Fuel Oil

Diesel

Jet Fuel

You will see they are all pretty much the same thing, some are just refined a little more and others have a few extra additives.
The "tidbit" in <a href="http://www.tfproject.org/tfp/showpost.php?p=2387703&postcount=24">post #24</a> was poster Byrnison's own opinion, possibly influenced by media reports and prior comments by NIST investigators, in their now, six years plus, long, and yet to be completed, investigation of the collapse of WTC 7.

I've posted the current NIST "working hypothesis", relevant excerpts from the transcript of their Dec. 17, 2007 meeting, and the time log points where the combustibles in WTC 7 are discussed by NIST, on Dec., 18. Listen to the audio and use my time points to minimize the time you have to spend.

The media covered the speculation of what fueled the WTC 7 fires, in the months following the 9/11 collapse, but they did not report on the new NIST disclosures.

Byrnison posted a now obsolete assumption.

Even in 2005, when NIST released it's 10,000 page report on this collpases of WTC 1 & 2, they were laying the groundwork for abandoning a hypothesis for "diesel oil fueled fires", in WTC 7.:

Quote:
http://wtc.nist.gov/pubs/WTC%20Part%...se%20Final.pdf

April 5, 2005


page 4

....NIST plans to release a draft of the final report for public comment in June 2005; public
comment period of about 6 weeks after release of the draft reports; NIST plans to release final
Investigation report in September 2005.
• WTC 7 report will be issued as a supplement to the main report: draft planned for October
2005; final for December 2005.
• Decoupling of WTC 7 report necessary to accommodate overlapping staffing demands for work
on WTC towers.
• This change affects mainly the collapse analysis; other WTC 7 work will be reported with the
other Investigation reports......


page 6

Working Collapse Hypothesis for WTC 7
If it remains viable upon further analysis, the working collapse hypothesis for WTC 7
suggests that it was a classic progressive collapse, including:


page 21

Observed Fire Locations (11:30-2:30 pm)
General
􀂉 No diesel smells reported from the exterior, stairwells, or lobby
􀂉 No signs of fire or smoke below floor 6 from stairwell and lobby areas
􀂉 Fire reported at west wall of floor 7 around 12:15 pm
􀂉 In east stairwell, smoke was observed near floors 19-20; signs of a fire
observed on floor 23
Looking from southwest corner to the south face
􀂉 Fire in SW corner near floors 10 or 11
􀂉 Fire on floors 6, 7, 8, 21, 30
􀂉 Multiple fires observed on floors numbered 20’s and 30’s
􀂉 Heavy black smoke coming out of south face gash; no fire observed
Looking from southeast corner to the south face
􀂉 Fire on floor 12;1 area above covered with smoke
􀂉 Fire on floors 11-121 moved to east face and progressed to the north
1 fires reported on floor 14, but photographs showed east face fires on floor 12


page 22

Observed Fires
East Face Fires on Floors 11-12 near 2 PM
Fires in WTC 7—which began soon after WTC 1 collapsed—were observed on Floors 7, 8, 9,
and 11 near the middle about half an hour before collapse; Floor 12 was burned out by this time.
Fires were also seen on Floors 12, 13, 22, 29, and 30 at various times during the day.

page 23

Observed Fires
North Face Fires on Floors 7 and 12
near 3 PM

page 29

Status of Initiating Event Analysis
NIST continues to evaluate the factors that could have caused column 79,
80, or 81 to fail
Possible contributing factors include:
􀂉 Damage to components adjacent to truss #2 from debris impact
􀂉 Damage to fireproofing from normal activities prior to event or debris
damage
􀂉 Unusual fuel loads (fuel lines, high density of building contents)
Analysis to date indicates:
􀂉 Massive size of columns 79, 80, and 81 appears to require severe
fires and/or damaged fireproofing to initiate thermally-related failures

page 38

Fuel System for Emergency Power in WTC 7
• NIST has reviewed and documented the fuel system for emergency power in WTC 7
• Floor 5—which did not have any exterior windows and contained the only
pressurized fuel distribution system on the south, west and north floor
areas—is considered a possible fire initiation location, subject to further data
and/or analysis that improve knowledge of fire conditions in this area.
• The two 6,000 gallon tanks supplying the 5th floor generators through a pressurized
piping system were always kept full for emergencies and were full that day.
• Both tanks were found to be damaged by debris and empty several months after the
collapse. Some fuel contamination was found in the gravel below the tanks and
sand below the slab on which the tanks were mounted, but no contamination was
found in the organic marine silt/clay layer underneath.
• This finding allows for the possibility, though not conclusively, that the fuel may have
contributed to a fire on Floor 5.

page 39

Observations on Fifth Floor
• Critical columns (79, 80, 81) carrying large loads from about 2,000 ft2 of floor area were
present on the 5th floor.
• The 5th floor was the only floor with a pressurized fuel line supplying the emergency power
generators.
• Two 6,000 gallon fuel tanks supplying a pressurized line possibly contributed to fires; tanks
were found to be damaged by debris and empty several months after collapse.
• In a 1997 facility condition survey, fireproofing was observed to be prominently missing on 5th floor
framing above main lobby; possible repair not confirmed.
• A majority of the 5th floor was not protected by sprinkler systems, with the exception of mechanical
space to east and office area to north side of building; no evidence of sprinklers in enclosures on
5th floor (also on floors 7, 8, and 9) which housed OEM generators and day tanks. Seventh floor
generator room may have been sprinklered, conflicting data.
• Two of the three sprinkler risers which were located next to stairs (#1 and #2) on the west side of
the building transferred towards center on the 5th floor along with stairs.
• Sprinkler systems on floors 1 through 20 were supplied directly from the city distribution system
through an automatic pump located on the 1st floor; water supply could be interrupted by loss of
power to fire pump or significant damage to underground city main in vicinity of building.
The above status was issued on April 5, 2005. 31 months later, NIST stated that it's working hypothesis involves ONLY "normal building fires", and NIST asnswered a question on Dec. 18, 2007, as to what those fires were fueled by; "normal"room contents, predicted to be 4 lbs, of combustibles, per square foot, consumed in moving fires, buring no more than 20 minutes in a given location, before completely consuming the combustibles.
host is offline  
 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360