Long story ... but big, unusual problems:

About 3 years ago we moved our IT department and server room into a brand-new state of the art building on campus. This building cost around 43 million dollars and has all the bells and whistles.

The server room is nothing different than most server rooms: separate A/C with backup; 15Kva power conditioner and UPS; natural gas generator with diesel backup. Nothing can go wrong ... right?

Well, during the first month we lost power to the room because the utility company was doing some work and severed one of the main feeds to the campus. No biggie right? The UPS and generator will keep us up and running. Nope. It all failed. Nothing like trial by fire. Room goes down hard. We go through and unplug everything because we don't know what's going to happen when power is restored ... good thing too.

We get the techs out here and they "fix" everything so nothing like this will ever happen again.

Power goes out again a few weeks later (rainstorm). Generator kicks in; but the vibration from the generator itself trips the earthquake valve which cuts off natural gas. No big deal - diesel should kick in any minute which sends an alarm to physical plant to call us and give us an hour to get back to campus and shutdown right? Nope. UPS batteries are depleted in 45 minutes. The UPS is supposed to send a graceful shutdown signal to the servers when it reaches 20% ... didn't happen. The room goes down hard.

Power is restored. The room comes up just as hard. We lose three servers because of the subsequent surges. Why is the power conditioner failing; shouldn't it be inline and protect us from surges? You'd think so. But it seems that the power conditioner fails "closed" when batteries are depleted. So when power is restored the servers are NOT protected but the power conditioner itself IS protected from surges.

The technicians for the power conditioner tell us that the device will protect itself from surges after batteries are depleted because it would "cost us a lot of money to replace it."

Hmmm, let's think about the logic here. We have paid around $30,000 for a power conditioner to protect $200,000 worth of equipment; but they have designed the conditioner to protect itself rather than the much more costly equipment downstream?

To make a long story short it took us two more power outages to get everything working the way it should. And I still don't trust any of it.
vanblah is offline  
 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360